Mr. B. Rhodes: Mr. Longbottom has done less than justice to large diameter strand, by which I mean 28 mm (1 1/8 in) diameter strand. I know it is not used a lot, but this is really because of lack of effort on the part of the manufacturers and the system suppliers. 28 mm diameter strand has certain basic drawbacks, namely:
1. The shape of the load/extension curve
2. Relaxation losses at 6 per cent
3. Lower grip efficiencies
4. The tendency to fly open when cut
5. The 'banana' effect at the ends

Additional information

Format:
PDF
Publisher:
The Institution of Structural Engineers

Tags

Opinion Issue 9

Related Resources & Events

The Structural Engineer
<h4>High Aluminia Cement Concrete in Buildings</h4>

High Aluminia Cement Concrete in Buildings

On 20 July last, under ref. BRA/1068/2, the DOE addressed the letter given below to local authorities, new town development corporations, etc. The letter contains an assessment of the BRE Report on the failure of roof beams at Sir John Cass's Foundation and Red Coat Church of England Secondary School, Stepney, and sets out a programme of action for inspection and assessment. Attached to the letter was an annex 'Suggestions for testing high alumina cement concrete' which is published on page 326.

Price – £10
The Structural Engineer
<h4>Discussion on Blow, Blow, thou Winter Wind, th'art Not so Unkind as Chap. V: Part 2 by Ronald G. Ta</h4>

Discussion on Blow, Blow, thou Winter Wind, th'art Not so Unkind as Chap. V: Part 2 by Ronald G. Ta

Professor S. Mackey (F) : My main concern is to learn why, in Britain, limited records of wind and pressure measurements are being extrapolated to such a degree that if applied to Hong Kong conditions would render economic design of buildings impossible.

Price – £10
The Structural Engineer
<h4>The Structural Assessment of Buildings Subjected to Bomb Damage</h4>

The Structural Assessment of Buildings Subjected to Bomb Damage

By any standards bomb damage is a messy business. Even when considered by the structural engineer back in his office and away from the debris and the broken glass, it is untidy and presents problems that are far different from those entailed in the design of new works. Peter S. Rhodes

Author – Rhodes, Peter S
Price – £10